I don't have my code book with me so my references are from memory, but here goes. The NEC states that wire terminations 100amps and below are considered to be 60-deg c and terminations above 100amps are 75-deg c, unless the equipment states otherwise. I hope I got that right. The UL Green Book has a listing for Molded Case Breakers that states breakers that are rated 75-deg c are to be applied at the 75-deg c rating only when installed in a separate enclosure with no other equipment. I have always used this information as follows: Breakers 100amps and below with a 60/75 deg-c rating are to be applied at 60-deg c when installed in a panel with other breakers and at the 75-deg c rating when installed in their own enclosure. I contacted GE applications and was told that GE breakers are rated to be applied at 75-deg c when installed in their panels. My problem is GE only provided breaker information and nothing that spoke directly to the installation of their breakers in panels and the UL Green Book of which GE is one of the manufactures listed, does not mention anything about GE breakers meeting any standard to allow them to be applied differently from that stated in the UL Green Book. Does anyone have any experience with this subject and how are you Engineers applying breakers with respect to the 60/75-deg c rating?