Went on a svc call yesterday...fixed the problem but also found this: Homeowner.. DIY'er installed a range ckt. He used 10/2 w/grd copper romex along with a 30A DBL P Square D Homeline breaker.
I turned the range on to full load and put an amp meter on it. I found: 35A-38A on each leg and the cdr was warm. The bkr did'nt trip after 10 min. I'm going to install the correct 40A ckt tommorow. (I understand the continuous load theory along with the cdr derateing theory). My question is: why did'nt the bkr trip? Was it because of +/- %tolerances?
I turned the range on to full load and put an amp meter on it. I found: 35A-38A on each leg and the cdr was warm. The bkr did'nt trip after 10 min. I'm going to install the correct 40A ckt tommorow. (I understand the continuous load theory along with the cdr derateing theory). My question is: why did'nt the bkr trip? Was it because of +/- %tolerances?