We have a new air compressor unit that has a 480V wye-delta starter. From a circuit breaker in the MCC we have one set of 4/0 cables going to to the main contactor in the compressor and the other set of cables going from the breaker and landing on the delta contactor of the compressor. So esentially the two sets of cables are actually part of the windings of the compressor motor and the line current is on the line side of the breaker. The compressor also has some auxiliary equipment that is tapped off of the delta contactor.
The breaker in the MCC that I am refering to is a 400A breaker, and I am now questioning if this breaker is adequate to protect this 4/0 cable. Assuming 4/0 is rated for 260A I could see that it would be possible for 260A to flow in these cables and thus not be protected by the breaker.
The part that is confusing to me is the fact that these cables are also part of the motor windings. The motor is only rated at 241FLA so the current that we should see in these cables is 139.3A, and I believe the auxiliaries are only a few hp. There is a motor overload set inside the compressor looking at the winding currents.
So even though these 4/0 cables I am referencing are actually part of the windings, and there is overload protection for the main motor is there still a code violation with having these 4/0 cables on a 400A breaker?
The breaker in the MCC that I am refering to is a 400A breaker, and I am now questioning if this breaker is adequate to protect this 4/0 cable. Assuming 4/0 is rated for 260A I could see that it would be possible for 260A to flow in these cables and thus not be protected by the breaker.
The part that is confusing to me is the fact that these cables are also part of the motor windings. The motor is only rated at 241FLA so the current that we should see in these cables is 139.3A, and I believe the auxiliaries are only a few hp. There is a motor overload set inside the compressor looking at the winding currents.
So even though these 4/0 cables I am referencing are actually part of the windings, and there is overload protection for the main motor is there still a code violation with having these 4/0 cables on a 400A breaker?