Hello...


I have two Distribution Board on my first DB there is a spare 63A,I will use this 63A breaker and run it to second panel. The second panel have a 100A as my main breaker connected on it are (2) 32A and (4) 25A, can I use that 63A to protect my 100A breaker? or should I upgrade the 63A breaker to a higher rating? What about about the cable size?

Thank you...

Eduardo
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
It is allowable to protect a larger breaker with a smaller breaker. If you keep your 63A breaker than you would not have to change the wiring. Only a load calculation can tell you if the 63A feeder is the correct size.
 

mikehughes8

Senior Member
Location
NC
Your probably in a situation with limited resources. In Iraq I dealt with this constantly. Putting a 63a breaker in series with a 100A breaker will never be a violation but may be deemed ridiculous. Make sure your load won't cuase a nuisance tripping on the 63A breaker.
 