So I know that a standard breaker is rated for 80% of its rating and 100% rated breakers are rated with an approved assembly for 100% continuous load.
But my question is with Non Continuous loads on a standard breaker. Is it still only 80%? And if so does that mean that there are 2 different deratings for the same load?
20 amp breaker can be loaded to 16 amps ...
But continuous loads need to be calculated first.
So a 14 amp wall heater @ 125% = 17.5 amps (more than 16) Can NOT be on a 20 amp breaker even though the 125% has already been accounted for. (its only pulling 14 amps)
I think the answer to my question is that there are 2 different rules happening here and they both have to be done to comply.
And with a 100% rated breaker... do you still need to add the 125% to a continuous load first as it is a different rule than the breaker rule? (the heater is still seen as 17.5 amps... NOT 14 amps)
Side question: Is a 100% rated breaker the same thing as a fully rated breaker in a series/fully rated system, or are these different products, Meaning if you wanted to not series rate and it was a continous load, do they make that combination in a breaker?
But my question is with Non Continuous loads on a standard breaker. Is it still only 80%? And if so does that mean that there are 2 different deratings for the same load?
20 amp breaker can be loaded to 16 amps ...
But continuous loads need to be calculated first.
So a 14 amp wall heater @ 125% = 17.5 amps (more than 16) Can NOT be on a 20 amp breaker even though the 125% has already been accounted for. (its only pulling 14 amps)
I think the answer to my question is that there are 2 different rules happening here and they both have to be done to comply.
And with a 100% rated breaker... do you still need to add the 125% to a continuous load first as it is a different rule than the breaker rule? (the heater is still seen as 17.5 amps... NOT 14 amps)
Side question: Is a 100% rated breaker the same thing as a fully rated breaker in a series/fully rated system, or are these different products, Meaning if you wanted to not series rate and it was a continous load, do they make that combination in a breaker?