Hi to All:
Question 1:
My chiller has FLA of 735 of which 718A is the compressor, 6.2A is for oil pump and 10A for controls:
I have calculated my overcurrent protection in the switchgear as follows:
(718x1.75)+6.2+10A=1272.2A. Can I use a 1200A breaker?
Manufacturer says that Maximum over current device is 1600A, but they are putting a 1200A rated non fused disconnect with the equipment.
What would the cable size from the breaker be?. I was going to put 1200A worth of cable.
The next question is: Is the 1200A caculated, should use a 100% rated breaker or not, and what if I used fuses?
Question 2:
There is an existing chiller, that all we know about it is that it is 1040 running amps.
a OCPD for both would be: (1040*1.75)+735=2555AMPS. cAN i USE A 2500A overcurrent device and does it have to be 100% rated
Thanks for the help