Amperage on the motor is 40.9A. Hp10.
I will insert an image of the nameplate.
Conductor size would be Amps x 125%, that would come to 51.125 amps. So I would need a #4 Aluminum or #6 copper correct?? But the question is how do I size the breaker with the inrush on the motor? Isn't it Amps x 225% then? That would come to 92 Amps with inrush. Can I use a 100 amp breaker? My conductors will be protected since I sized them accordingly. Thanks.
Sent from my SM-S911U using Tapatalk
I will insert an image of the nameplate.
Conductor size would be Amps x 125%, that would come to 51.125 amps. So I would need a #4 Aluminum or #6 copper correct?? But the question is how do I size the breaker with the inrush on the motor? Isn't it Amps x 225% then? That would come to 92 Amps with inrush. Can I use a 100 amp breaker? My conductors will be protected since I sized them accordingly. Thanks.