Customer has a 30 KVA, 3-Phase, 480v Delta - 208Y/120v transformer. It is reverse feed with a 60 amp breaker on the 208v side and #10 wire coming from the 480v side feeding a machine. I don't remember the fuse size at the machine.
They called because the machine lost power. I found the 60 amp breaker tripped and priced the job to replace the transformer because I thought the transformer was bad.
I've done some research tonight to find out that the inrush when you reverse feed a transformer is really high so I'm thinking that that 60 amp breaker is to small and that is why it tripped.
What size should the breaker be on the 208v side to reverse feed this transformer and handle the inrush?
They called because the machine lost power. I found the 60 amp breaker tripped and priced the job to replace the transformer because I thought the transformer was bad.
I've done some research tonight to find out that the inrush when you reverse feed a transformer is really high so I'm thinking that that 60 amp breaker is to small and that is why it tripped.
What size should the breaker be on the 208v side to reverse feed this transformer and handle the inrush?