In other words, the disconnect with fuses would not work. Gotcha.
Not sure what type of ground detector to get and how I would connect it. I guess I could just ask the supplier and it would probably connect to the disconnect.
Check "Bender" ground detection devices.
Also, be prepared in the future to get a call back when the 80A breaker trips; eventually. The issue is that the inrush is independent of load. It is a characteristic of the core saturation. The curve indicates even a 100A breaker may not be sufficient. You could turn it on and off 100 times and it works fine, on the 101 it will trip, or you could turn it on once and it trips, then 30 more times it won't. Just depends on where the zero crossing end ups when it was de-energized.