jim dungar said:this 80% effect matches exactly with the NEC rule for 125% conductor protection.
210.20 (A)?
Sorry about the dots. Should I start using metric? :grin:
jim dungar said:this 80% effect matches exactly with the NEC rule for 125% conductor protection.
General design philosophy acording to carl (recognized as no more valid than anyone else's). Some exceptions apply.[/qoute]
I mean how can you not like this guy, I want to meet Carl.
frizbeedog said:210.20 (A)?
Sorry about the dots. Should I start using metric? :grin:
jim dungar said:Among other locations (i.e. NEC2005 450.3).
coulter said:General design philosophy acording to carl (recognized as no more valid than anyone else's). Some exceptions apply.
Basic premise: Something broke or the fuse wouldn't have blown.
OPC doesn't protect the device. The device is protected by design. If the device goes bad and draws too much current, what is there to protect? - remember, "the device goes bad".
carl
I'll agree with that - for industrial. The more expensive the motor, the more protection one hangs on the motor to save as much as possible.bikeindy said:I'll agree with your basic premise that something broke, it doesn't mean the motor is bad and that trips the breaker the mount holding the motor could fail and the motor bind causing an overload if the breaker is rated for the wire the motor may now fail if the breaker is rated for the motor it will not fail.
brian john said:As with all of us telling the truth - plenty of reasons. But thank you (I thinkGeneral design philosophy acording to carl (recognized as no more valid than anyone else's). Some exceptions apply.[/qoute]
I mean how can you not like this guy, I want to meet Carl.)
carl
lmchenry said:So my next question, is it possible to have a pc of equipment that is fastened in place and have a noncontinuous load of say 28 amps on a 30 amp CB? Give me some help I am trying to think of one.
lmchenry said:Thanks for all the feedback. Let me draw some conclusions. CB's are not just for conductor protection. They often protect equipment and determine the actual circuit rating. So my next question, is it possible to have a pc of equipment that is fastened in place and have a noncontinuous load of say 28 amps on a 30 amp CB? Give me some help I am trying to think of one.
coulter said:Give me an example of a residential motor that could overload under normal operation, that the OCP would save - I'm sure there are cases, I just can't think of any.
I don't know. It's got a thermal in it - saved by design?dtiller said:Garbage disposal?
lmchenry said:as far as the range it is cord and plug connected and restricted by 210.23 a1