kyleapec
Member
- Location
- siloam springs arkansas
I apologize for stepping out so long been busy with the wife and kids for the holidays. I appreciate all of the input. All of the wire sizes for these VAV'S will be quite oversized (I learned something new on this project about having to assume 60 degrees when when the temp rating of the equipment is unknown) so were fine on the ampacitys (#8 for the example used) . I wrote them a change order because I assumed that the OCPD needed to be at least larger than MCA, they did not want to pay it and said to leave it. It definitely is not the way I would like to build a building but I wanted to get some input from you guys. Back to post #7 from INIFNITY.
"You do not need to use the MaxOCPD but you do need to provide a circuit that is at least as large as the MCA. Even though a 35 amp OCPD will most probably work it still isn't code compliant. What size conductors are you planning on using?"
Do you have any code references towards that? I assumed that was the case, but i couldn't find anything in the code saying that. Looking at post #14 from Little Bill, I believe that is exactly what the engineer is saying, but I still think it's not right (maybe a 110.12 violation ) Thanks again for all the input guys.
"You do not need to use the MaxOCPD but you do need to provide a circuit that is at least as large as the MCA. Even though a 35 amp OCPD will most probably work it still isn't code compliant. What size conductors are you planning on using?"
Do you have any code references towards that? I assumed that was the case, but i couldn't find anything in the code saying that. Looking at post #14 from Little Bill, I believe that is exactly what the engineer is saying, but I still think it's not right (maybe a 110.12 violation ) Thanks again for all the input guys.