Equipment MCA is 22A
MOCP is 35A
We installed L6-30R to match equipment L6-30P cord and fused with 30A breaker.
Inspector failed final, said must have a 35A breaker, and must go to next size recep which would be 50A; will also have to change cord.
Conductors are #8 as equipment schedule showed 40A unit going in, but details noted to verify nameplate. It did show a receptacle connection, but no details on recep type other than "250v".
Is this accurate?
I always thought you only needed to clear MCA.
Sent from my iPhone using Tapatalk
MOCP is 35A
We installed L6-30R to match equipment L6-30P cord and fused with 30A breaker.
Inspector failed final, said must have a 35A breaker, and must go to next size recep which would be 50A; will also have to change cord.
Conductors are #8 as equipment schedule showed 40A unit going in, but details noted to verify nameplate. It did show a receptacle connection, but no details on recep type other than "250v".
Is this accurate?
I always thought you only needed to clear MCA.