When running (2) 12/3 feeders for a kitchen. One feeder is for the SA receptacles, both 20A breakers. The other feeder is one leg for lighting and the other leg for the dishwasher. My question is if lighting gets a 15A breaker, can a 20A breaker be used for the dishwasher leg or do both breakers have to be the same amperage rating. Like 15A for both? I read through 210.4 but can't find it in there.