breaker sizing
rose1981
TX
Attached is the cut sheet for RTU. MCB is 25Amps. Should I go with 25amps breaker or should I size? Can someone please tell me how to do the calculation for breaker sizing for this particular equip?
  • RTU-1.pdf
25 amp breaker is as large as you can go by nameplate, therefore as large as you can go by code.
all the calculations have been done.
I would run #12 and put it on a 25 amp breaker.
I just noticed it has an 18kw heater. Is that another circuit that's required? If not 35 amp is your maximum
IN agreement with one unlikely caution. Bring an RTU I doubt you are running NM, but in case you are and if you are under the '14 Code, I think the 60° rating on #12 in now 20 amps so #12 NM under the '14 would not be allowed for your 21.6 load.
Wow Gus, I wasn't aware that NM fell under the temperature limits too. Thanks. I would have made that mistake.