Breaker sizing

mannyb

Senior Member
Location
Florida
Occupation
Electrician
Can #1copper be used with 150a breaker being same size up from 125a per nec 240. The feeder is under the 800a
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
** There are exceptions to being able to round up, like taps.

But yes, what you mentioned sounds okay!
 