nyerinfl said:
Stealing your 33.19 answer as I don't want to do the math again, since it's for an instantaneous CB, wouldn't the next step be to size it 250%, which would give 83A, next size up it and you have a 90A CB.
The question is not entirely clear, so some assumptions must be made. The facts:
three phase motor, 7.5 HP
Motor temp rise of 38C
Assumptions:
The question asks for the size of "Breaker." This would be short-circuit/ground-fault protection. Since this is a three phase motor, the assumption is that this motor is using a starter that has separate overload (heater/relay) and short circuit elements.
Since the temp rise is given as less than 40degC, we are allowed to use 125% of nameplate current in order to size the overload element. But this is not a part of the problem. If they had wanted this, they would have had to have given us the nameplate current, which they did not. Further evidence that what they wanted was the S.C./G.F. protection.
So, assuming the motor is 460 V, 7.5 Amps. The FLA (430.250) is 11.
The Motor branch circuit is 125% of this, or 13.75 Amps. We can use just about any size wire for this, but let's just use 12 AWG.
The overload relay has to be dialed to a setting of 125%, or the same 13.75 Amps.
The short-circuit/ground-fault protection, since an Inst. Bkr. is being used, is 11 * 8 = 88, next size up, 90 Amps. (another assumption here, that the motor is not Design B)
You can see that the branch circuit conductors are really protected by both the overloads and the SC/GF devices. The overloads are set to the same ampacity that must be carried by the conductors.