Can single pole breakers be converted to two or three pole units by the use of tie handles? If this is permitted - can a standard screw be used to tie the handles together?
I would also like to point out that in the 2011 NEC 240.15(B)(2) and (3) have been change to indicate that single pole breakers utilizing handle ties for overcurrent protection of line to line loads are limited to 120/240 volt circuits.
Wait a sec ... I didn't think that you could do this in the first place!
Why did you think that?
Roger
As long as the loads are line to neutral, 240.15(B)(1) allows handle ties.
internal vs external trip devices? Do you have code referance(s) for thisMy opinion is that it depends on the Code wording. In some cases, such as 450.5, the Code calls for common-trip which would require internal mechanics. In other cases, such as 210.4, the Code calls for simultaneous disconnect and a handle tie can be used.
Most inspectors that I know will not accept "home-made" means such as screws or wires to establish simultaneous disconnect.
As long as the loads are line to neutral, 240.15(B)(1) allows handle ties.
Yup ... see few posts up though. It says line to line.
Yup ... see few posts up though. It says line to line.
(3) 3-Phase and 2-Phase Systems For line-to-line loads in 4-wire, 3-phase systems or 5-wire, 2-phase systems having a grounded neutral and no conductor operating at a voltage greater than permitted in 210.6, individual single-pole circuit breakers with identified handle ties shall be permitted as the protection for each ungrounded conductor.
internal vs external trip devices? Do you have code referance(s) for this
...and will not cause the other breakers tied together to trip when 1 breaker trips under overcurrent.
While I agree that the code requires a device identified for the purpose and an inspector has a good code reason to not accept a home made solution, a 6-32 screw with nuts provides a far more secure handle tie for two QO breakers than does the factory supplied identified for the purpose device.... Most inspectors that I know will not accept "home-made" means such as screws or wires to establish simultaneous disconnect.
While I agree that the code requires a device identified for the purpose and an inspector has a good code reason to not accept a home made solution, a 6-32 screw with nuts provides a far more secure handle tie for two QO breakers than does the factory supplied identified for the purpose device.
I also agree that the handle tie only provides a common means of disconnect, it does not create a common trip breaker.
If I encounter one of the 6-32 arrangements you describe, it looks "factory" to me . A piece of #12 bent on both ends does not.
Dog gone it, now I have to go change something in my panel at home. :grin:
Roger
If your panel is representitive of 90& of the panels I have seen in electricians (and inspectors) homes, I bet that handle tie would not be the only eyebrow raising sight :grin: