I'm trying to get a 200 amp breaker with a instantaneous magnetic trip setting of 3000 amps.
View attachment page 1.pdf View attachment Page 2.pdf View attachment page 3.pdf View attachment page 4.pdf
Here I'm looking at the PDF page 4.
If I understand this right, In is the breaker frame size, and Ir is the trip current setting. So a 400 amp breaker with the trip setting at 0.5 would have In = 400 amps, and Ir = 200 amps.
Since the instantaneous ratings are based on In, that breaker could have its instantaneous rating set for 10x the 400 amps, which would be 4000 amps. Does that sound correct? Or would it be 10x the 200 amp setting, for a total of 2000 amps?
If the 10x 400 amps is correct, I know the tolerance only guarantees me 8x, which is 3200 amps, and still above the 3000 amps I need.