I agree!! But, i?ll go take a look Weds!!MCA is for wire size.
MOCP is for breaker/fuse size.
If MCA is 44.9, I'm pretty sure the MOCP is AT LEAST 50A. Most likely 60A
You can downsize the breaker to 40A, but with an MCA of 45 I think you'll have problems with breaker tripping.