What I tried to do in my previous post wp outas to avoid needless time that is waisted to calculate actual fault current which may not gain you anything such a going from a 14kaic breaker to a 30kaic breaker. If the actual kaic based upon he available fault current based upon unlimited fault current on the pri. Is equal to or below that breakers kaic rating you can stop there but you still must consider the beaker ratings down sterean. As they too mî
Sorry, my post was incomplete as I had to step away it timed out N me.
What I tried to do in my previous post was to avoid needless time that is waisted to calculate actual fault current which may not gain you anything such a going from a 14kaic breaker to a 30kaic breaker. If the actual kaic based upon he available fault current based upon unlimited fault current on the pri. is equal to or below that breakers kaic rating you can stop there but you still must consider the beaker ratings down sterean. As they too must have a. Kaic ratiing equal honor less than than the faultcurrent that the main breaker was based upon which is called being fully rated. Should hat a value be above then you will find coordination study to determine what the actual available ka would be at each one of the down stream breakers and gthrogh th same considerations you did ewhen justifying the main faic rating.
The key is to never needlesly taking the time to do ka calculation if it doesn't gain you anything. If you go from a 14kaic to a39kaic device and the max ka at the transformer secondary is 28ka then busting your butt to calculate 25 or 26ka is not going to change the 30kaic rated breaker. Doing a coordination study only gains something only if the ka is above the 30kaic rating and you need to consider going up to a 42kaic, the next higher rated device. In taking the time to do a coordination stidy there may be a chance that the actual available ka at the device is less than the kaic rating of the device which then justifies the need not to go up to a 42kaic device.
Without doing a coordination study all devices down stream of the main breaker must be fully rated for the available ka where each device is located.
If luck is on your side the devices down stream from the main breaker may have a "series rating" with it which may justify the need to have to up to athe next higher kaic rated device.
This may have been a long post but this is the thought pattern that must be considered when justifying he kaic ratings of each device when changing the available ka current at the service entrance.