Breaker & Wire Size

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Can you have FUSED 200A switch feeding load with #8 wire? Doesn't wire need to be rated ampacity to match switch size?
 
Last edited:
could be OK if it is a legal tap conductor. biggest problem might be that the lugs on the 200 A switch are not listed for use with a #8 wire.
 
Question is what's the input current. Don't know.
No way for you to know without more input (RFI) or on-site inout BUT as noteds, with a 50 amp wire and 430.122 it's practically impossible that it would meet Code unless it'sa tap to another OCP device and meets 240.21
 