Can you have FUSED 200A switch feeding load with #8 wire? Doesn't wire need to be rated ampacity to match switch size?
Last edited:
AC unit with VFD and disconnectProbably not but what kind of breaker and what kind of load?
Conductors have to be sized to 125% of the input current of the VFD. With a 200 amp OCPD I doubt that #8 is the correct size.AC unit with VFD and disconnect
Question is what's the input current. Don't know.Conductors have to be sized to 125% of the input current of the VFD. With a 200 amp OCPD I doubt that #8 is the correct size.
No way for you to know without more input (RFI) or on-site inout BUT as noteds, with a 50 amp wire and 430.122 it's practically impossible that it would meet Code unless it'sa tap to another OCP device and meets 240.21Question is what's the input current. Don't know.