Can you have FUSED 200A switch feeding load with #8 wire? Doesn't wire need to be rated ampacity to match switch size?
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Question is what's the input current. Don't know.
No way for you to know without more input (RFI) or on-site inout BUT as noteds, with a 50 amp wire and 430.122 it's practically impossible that it would meet Code unless it'sa tap to another OCP device and meets 240.21
 