Breakers size
ohmhead
ORLANDO FLA
Well question motor circuit 100 hp fla on name plate 111 amps 3 phase 480 volts no voltage drop needed .
wire 4/0 copper thwn-2
motor has a starter with overload protection
2 inch conduit rigid
What is the largest breaker protection you can put on this circuit just a general question to wire size to breaker size ?
wire size to breaker size !
Due to the various exceptions it is not really that easy to pin it down but ....
100 HP 460 volt motor.
Per Table 430.250 that motor has a load of 124 amps. (forget the nameplate FLA for breaker sizing)
Per Table 430.52
Max Non Time Delay fuse = 400
Max Time delay fuse = 225
Max Inverse Breaker = 350
Max Instanious breaker = 1000
Motor branch circuits do not need wire ampacity to match the overcurrent device amps. Your 100 hp motor needs a minimum of 155 amp conductor but depending on what type of overcurrent device you have it could be rated well above that.
The conductor is still protected from short circuits and ground faults by the fuse or breaker and is protected by overloads by the overload protective portion of the motor controller.
Per Table 430.52
Would it matter if it went thur a vfd drive or would this be the same iwire ?