BINGO !!! I fall for this every time. I trust my supply house to give me the right parts when I place an order. I was doing rough-in work so I never thought to open the panel cover. 1st item says "use BRPHD" hold-down kit." I've said this numerous times - "You have to pay for your education." Thanks for setting me on the right path.Does the loadcenter door show it will accept the hold down accessory?
As far as know hole in the breaker I really surprised the breakers don't have the hole. Can you post a picture of the breakers? Trying to make a hole in the breaker in the field would destroy the breaker. As I mentioned previously the breakers are manufacture with notches on each have that when sandwiched together make the hole.