If that was the case, then the table should say:I don't read that at all
If you use B2 with any stranded conductors you may not have more than (4) #12, but if you use only solid conductors you can have (5) conductors. While B4 allow the same quantity of both.
Guess its time for someone to 'ask the manufacturer'.
2-4 #12
2-5 #12 SOLID
If they don't specify solid or stranded, then you can use either. If they specify one or the other you are limited to that type.
With that said, I went to the manufacturer product page:
BCAP Wire Connector Model B2 Red
B-Cap-B2: Low profile design gets you into tight spaces and hard-to-reach spots comfortably Slim, classic fins offer a secure grip for extra leverage and easy installation Live-action spring of the Red B2 easily handles 2 #18 up to 5 #12, and will even de
www.idealind.com
The first .pdf linked on the B2 product page:
Has the only solid or only stranded restrictions we've been discussing (page 8 for the B2)
The second .pdf on the page:
Does not have the restrictions; it simply says '2-4 #12' for the B2.