If the tool instructions specified the manufacturer and part number of the connectors that it can be used with, I would be ok with that.
The code does not regulate the use of tools just products 90.1(C).
According to the UL 486C listing the only time you need to use a specific tool is if the manufacturer states it. Part of it may be included with same manufacturers tool or tool case but not different mfr's tool.
Unless that buchannon box states a specific tool is required that old school electrician is free to judge the sutibility of any blunt object for making the crimp (wether or not the tool idintifies the crimp).
If panduit or T&B say to use a specific tool then thats
the only tool to use with that crimp, if they dont stipulate a tool then anything goes, because UL has tested the crimp with tools they deem an electrician would have selected as described in my earlier post.
UL 486C Section 25 Marking:
25.14 A procedure that must be followed for proper assembly of a wire connector to a conductor shall be
described as follows:
a) Use of a Specific Tool Required ? When a connector is intended to be connected to a
conductor or conductors by a specific tool,...
See also UL white book ZMKQ:
white book (C) UL 2013 UL said:
INSTALLATION INSTRUCTIONS
Use of specific tools ? A specific tool and die used to assemble a wire
connector to a conductor is identified on the connector, or on or within the
unit container of the connector. The identification consists of a catalog or
type designation, color-coding, die index number, or equivalent means.
Color-coding of the crimp barrel is common.
Cheers and happy crimping