Mr. Retirede
Can I ask a question.
This will show my ignorance about buck boost transformers.
If I want to use a transformer primary 120v secondary 240v to run a 20 amp load which RLA/FLA are likely about 13 amps. Would a 5000Watt or 5kva transformer do the job? Considering the LRA that would spike for a split second before going down to FLA.
Also, if the primary amperage is typically twice the secondary amperage would I need to make sure the circuit breaker for the 120 primary is a 40 amp breaker since the secondary 240v would be 20 amps?
The last question is, will the buck boost transformer secondary have two hot legs of 120 volts each or will it have one hot leg of 240 v and the other leg neutral/common. I've noticed that the only step-up transformers I can find are with secondary of one hot leg 240v and the other common.
I need L1 and L2 to be 120v each for the 240volts.
Such is my lack of knowledge with buck boost transformers.
Thanks in advance.
Marik
Thanks for responding.
You guessed it.
I'm trying to run a portable A/C unit.
I'm putting together a roll around A/C unit that I can roll from site to site, classroom to classroom which makes it hard to find 230v power since most rooms only have 120v receptacles.
I'm guessing the circuit breaker for the 120v primary would have to be a 40amp circuit breaker to make the 240v secondary 20amp of the transformer work. Is that correct?
Is it also correct that for a 20amp secondary I would need about a 5kva transformer?
And would this transformer handle the LRA if the FLA/RLA were around 13 amps?
My other question is, would the 240 secondary have L1 and L2 each having 120v or would one leg have 240v and the other be common?
I need the USA standard of two hot legs.
I'm afraid this will be too expensive and I would be better off to find a 230 power supply.
This is for teaching purposes for HVAC students and as you can guess 230 volts isn't easy to find in a classroom.
I want your feedback even if it makes me look like an idiot.
Thanks
Mark