Exactly….
There is no isolating transformer and we are only seeking to buck the voltage down 10 to 12 volts (5%).
The transformers will be connected as autotransformers, carrying only a portion of the total load.
There is no specific target, we just need to get away from the inverters' high voltage shut down limit.
The Schneider / SquareD rep told me today…..
The losses are approximately: 90 watts @ NO LOAD + 135 Watts @ LOAD = 225 Watts fully loaded and operating.
Thanks!
Thanks for coming back to clear things up.
FYI, you don't even need 2 transformers to be able to transfer 30kW. You just need 1:
Rated amps at 12V winding (series winding) of your transformer = 3,000/12 = 250A
So, your rated kVA at 250V side = 250 X 250 = 62.5kVA!
Your voltage at the inverter side will be = 250VAC X 240/(240+12) = 238.1 VAC
Checking:
rated power = 238.1 X [250A + (3,000/240)] = 238.1V X 262.5A = 62,500 VA~ 62.5 kVA -> checks out!
On the original query re losses, please be reminded that when opting for an autotransformer configuration, your transformer impedance will not be the nameplate value as a single-phase unit. The autotransformer impedance will be a lot smaller:
%Z
autotransformer = %Z
single-phase x [1-1/TR], where, 1-1/TR = co-factor and TR =250V/240V = 1.0417.
%Z
autotransformer = %Z
single-phase x (1-0.96) = %Z
single-phase X 0.04
The losses when connected as an autotransformer will then be a lot smaller. That 225W losses is too high, (3,000-225)/3,000 = 92.5% efficiency!
Lastly, be aware that the available fault current of the autotransformer will now be greater than it was connected as two-winding transformer!