LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
The units in the OP are clearly wired L-N, not L-L.1. Since the three buck/boost transformers are all connected L-L, there is no reason for a neutral connection on the line side for the resulting autotransformers to work properly.
If the autotransformers were wired L-N, then a neutral would definitely be required, although a floating wye point would tend to float near ground.