kwired
Electron manager
- NE Nebraska
- EC
You can't use just any ol buck boost transformer. It does need VA rating selected in accordance to the load and amount of voltage change that needs to occur. But the basics of getting 240 out of 208 input are the same with a 16/32 secondary, you will need to put 32 volt coil in series with a 208 volt coil with the net across the series being 240. The fact the primary is rated 240 and not 208 probably changes actual result some but you will be in the right ballpark with actual output.. It’s on a pole and I only have single phase at the pole. 2 hots and a ground. That’s all. This buck boost transformer is not three-phase it is single phase. The panel is 208/120 single phase, the object they are trying to hook up is 240 single phase. I was given the buck boost transformer and was told to feed the xfmr from the existing 208 panel into the secondary side of the buck boost transformer which is 16/32. Then was told the primary would then have 240. Ive never hooked one up backwards. It just trips the breaker and I can find no reason why unless the xfmr is bad.
By putting 208 volts directly to the 16/32 coil the impedance is way too low and high current flows and reason you are tripping breaker. No OCPD and you would have burned it out, still possibly did some damage to it anyway.