G GlennG Member Location Hicksville, NY Mar 23, 2011 #1 Would there be any issues feeding a buck booster with a multi-wire circuit? 3 phases and a neutral. I have 208v and need 240v.
Would there be any issues feeding a buck booster with a multi-wire circuit? 3 phases and a neutral. I have 208v and need 240v.
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Mar 23, 2011 #2 Are you needing the neutral after the increase in voltage? I believe you can use two BB , open delta, to raise the L-L voltage but two legs (1&3)would be higher volt to ground. The third (2) would stay the same. Acme Transformer diagram BB and CC.
Are you needing the neutral after the increase in voltage? I believe you can use two BB , open delta, to raise the L-L voltage but two legs (1&3)would be higher volt to ground. The third (2) would stay the same. Acme Transformer diagram BB and CC.