puckman said:does anyone know how to size a buck-boost transformer to get 3 phase 220 to 230 volt from 3phase 240 volt . the load is 75 amps. 240volt is to much voltage.
mdshunk said:208 to 230 plus or minus 10% is 187 to 253. No problem. No buck-boost needed. Just make sure the tap on the 24 volt control transformer in the RTU is properly set.
Marc, unless the condenser fan is also 3-phase, how do you do this?mdshunk said:. . . I do . . . comfirm the rotation of the RTU.
LarryFine said:Marc, unless the condenser fan is also 3-phase, how do you do this?
I've been under the impression that 3-phase compressors, at least of the piston type, work equally well turning in either direction (but this may not apply to scroll compressors, if there even are 3-phase scroll units).
I'm asking because I will be re-connecting an older, small 3-phase RTU shortly, and if I'm not mistaken, the fan is only single-phase, so I won't have any clue as to which way the compressor will run upon energization.