- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
There is an existing space, a small lab that has mostly computer-type equipment (120V). I am designing a change to its power source. It has a few oddities that I need to deal with. Let me present two questions now, and I may have others later.
Situation: There is a 120/208V, three phase panel, from which a 50 amp, two pole breaker presently supplies ?normal? power to the lab. Immediately above the 120/208V panel, there is a buck/boost transformer. I do not understand exactly how such things are wired, nor how they operate. There is a backup generator (120/240V), a transfer switch, a UPS, a bypass switch, and some other stuff, all of which we will ignore for now. All of this stuff provides power to a 120/240V, single phase panel, and all lab loads are fed from there.
We all know that upstream of the buck/boost, the voltages will be:
? L1-N at 120V,
? L2-N at 120V, and
? L1-L2 at 208V.
Question 1: I believe that downstream of the buck/boost you will have L1-L2 at 240V. But do you still have 120V line to neutral on both lines?
Question 2: Upstream, L1 and L2 are separated from each other by 120 degrees. Will the buck/boost cause a further 60 degree phase shift, so that from that point downstream it looks just like any standard 120/240V single phase distribution system?
Situation: There is a 120/208V, three phase panel, from which a 50 amp, two pole breaker presently supplies ?normal? power to the lab. Immediately above the 120/208V panel, there is a buck/boost transformer. I do not understand exactly how such things are wired, nor how they operate. There is a backup generator (120/240V), a transfer switch, a UPS, a bypass switch, and some other stuff, all of which we will ignore for now. All of this stuff provides power to a 120/240V, single phase panel, and all lab loads are fed from there.
We all know that upstream of the buck/boost, the voltages will be:
? L1-N at 120V,
? L2-N at 120V, and
? L1-L2 at 208V.
Question 1: I believe that downstream of the buck/boost you will have L1-L2 at 240V. But do you still have 120V line to neutral on both lines?
Question 2: Upstream, L1 and L2 are separated from each other by 120 degrees. Will the buck/boost cause a further 60 degree phase shift, so that from that point downstream it looks just like any standard 120/240V single phase distribution system?