What was their panel statement?
I submitted 3 PIs:
1) 225.30 Change the title to "Number of Branch Circuit or Feeder Supplies." to make it clear there was no prohibition on a service as well.
CMP response: The proposed revision does not add clarity because this is already in the article referring to outside branch circuits and feeders.
That can be seen as saying the change would have no effect, because it's already clear there is no prohibition on a service as well.
2) 225.30 Opposite effect: change to "A building or other structure that is supplied by a service, branch circuit or feeder shall not be supplied by another branch circuit or feeder unless permitted in 225.30(A) through (F)."
CMP response: "The building is only served by a branch circuit or feeder and not a service. Services are not included in the scope of Article 225."
The first sentence could be seen as saying the building couldn't also be supplied by a service, while the second sentence suggests the opposite.
3) 230.2 Equivalent change to (2) above: change to "A building or other structure supplied by a service, branch circuit, or feeder shall not be supplied by another service unless permitted in 230.2(A) through (D)."
CMP response: "Article 230 addresses service, and does not include feeders and branch circuits."
This suggests that it's fine to have one feeder and one service without needing to meet any of the specified conditions.
Cheers, Wayne