A client, for whom my company often does work, asked me about an issue they are having. They have a major industrial campus and a group of their buildings receives measured voltage from the utility in the range of 495V-500V. This is on a nominally 480V service.
I have been around this campus for two years and I always have known that this was the case. I remember when I first joined, I questioned this and no one really seemed concerned.
Anyway, over the past couple years they have had some incidents that seem to tie back to this overvoltage situation. First, an elevator motor failed and the service repair guys blamed the voltage. Then an air compressor failed and service repair guys also blamed it on the voltage. They asked for my advice and I told them to ask the utility. But when they pushed back on the utility, the utility claimed the voltage delivered was within the approved tolerances. And I suppose 500V is only 4.2% above 480V.
BUT, I am just wondering if anyone has seen this before and if people think this is acceptable.
I have been around this campus for two years and I always have known that this was the case. I remember when I first joined, I questioned this and no one really seemed concerned.
Anyway, over the past couple years they have had some incidents that seem to tie back to this overvoltage situation. First, an elevator motor failed and the service repair guys blamed the voltage. Then an air compressor failed and service repair guys also blamed it on the voltage. They asked for my advice and I told them to ask the utility. But when they pushed back on the utility, the utility claimed the voltage delivered was within the approved tolerances. And I suppose 500V is only 4.2% above 480V.
BUT, I am just wondering if anyone has seen this before and if people think this is acceptable.