I'm new to the forum, so if this has been asked before please accept my apologies, but I have a strict time requirement and don't have time to search the archives.
The question is: What is the maximum service amperage allowed by the NEC on a building with 480v/3ph? Shown below is an e-mail excerp I received concerning this. The writer states that the cose limits 480v services to 700 amps. Is this true? I will be looking though the code while awaiting a reply. I would like some other opinions to back me up. I jnow of quite a few manufacturers that are in violation if this is so.
Thanks
barryh
The drawing shows a 480V, 3-Phase, 60 Cycle, 4-line
> service. I can't meet code however, with 480 Volts concerning ampacities.
> We need to get about 1100 amps at 480 volts into the building to service
> 2-350 HP pumps (future size) running simultaneously, plus all the other
> loads. NEC won't allow ampacity over about 700 amps/480V with even the
> largest sized wires.
> If we go with a higher voltage, which seems to be the right thing to do,
we
> should try to meet a standard motor size for the pumps. The two standard
> motor sizes above 480 volts are 575 and 2300 volt motors. I could use
some
> help on what step-down transformer should be used to meet these standard
> motor sizes in voltage.
The question is: What is the maximum service amperage allowed by the NEC on a building with 480v/3ph? Shown below is an e-mail excerp I received concerning this. The writer states that the cose limits 480v services to 700 amps. Is this true? I will be looking though the code while awaiting a reply. I would like some other opinions to back me up. I jnow of quite a few manufacturers that are in violation if this is so.
Thanks
barryh
The drawing shows a 480V, 3-Phase, 60 Cycle, 4-line
> service. I can't meet code however, with 480 Volts concerning ampacities.
> We need to get about 1100 amps at 480 volts into the building to service
> 2-350 HP pumps (future size) running simultaneously, plus all the other
> loads. NEC won't allow ampacity over about 700 amps/480V with even the
> largest sized wires.
> If we go with a higher voltage, which seems to be the right thing to do,
we
> should try to meet a standard motor size for the pumps. The two standard
> motor sizes above 480 volts are 575 and 2300 volt motors. I could use
some
> help on what step-down transformer should be used to meet these standard
> motor sizes in voltage.