Hello, my favorite community. I ran into a building a few days ago and its electrical setup confused me and seemed off. Trying to understand why they did it that way.....
You had a electrical meter outside that has utility cables coming from underground to it that was rated for 3#3/0 (200A) ------ Then the cables went into an interior disconnect box (in the room behind it) that was being used as a junction box when i opened it up. But in that junction box now there is 5#3/0 (400A), those 5#3/0 goes into the building main panel 4hot and 1 neutral that was rated 400A. Clearly they added cable sets to make the cables rated 400A for the panel at the meter, but why just 1 neutral wire? and why is there no ground wire? Is that code compliant when they did it in the older day? (this is an old building). I'm also not sure why they needed the junction box when they could of just ran the conduit to the main panel right next to it. See pics and riser below.
Thank you,


You had a electrical meter outside that has utility cables coming from underground to it that was rated for 3#3/0 (200A) ------ Then the cables went into an interior disconnect box (in the room behind it) that was being used as a junction box when i opened it up. But in that junction box now there is 5#3/0 (400A), those 5#3/0 goes into the building main panel 4hot and 1 neutral that was rated 400A. Clearly they added cable sets to make the cables rated 400A for the panel at the meter, but why just 1 neutral wire? and why is there no ground wire? Is that code compliant when they did it in the older day? (this is an old building). I'm also not sure why they needed the junction box when they could of just ran the conduit to the main panel right next to it. See pics and riser below.