POCO opinion....I see two conduits coming out of the bottom of the meter enclosure...one must be input from the transformer and one must be out to a panel. The disconnect shown has no OCD and also switches the neutral, so it could not be considered a service disconnect and would not be allowed. I'd likely shoot it down and require a service disconnect (OCD) at the meter (that means a GEC, ground rods and MBJ also at the meter) , then anything downstream would be up to the local AHJ and not the POCO. Most utilities have their own requirements that may exceed the NEC minimums. EUSERC does not allow a disconnect ahead of a single meter, and disconnects ahead of 2 to 6 meters is up to each utility that uses EUSERC as its requirements. One other reason we'd like it done our way is that we would not be responsible for the service wires from the meter to any remote service disconnects. I'd check with them. If all that is old news...never mind.