Building shunt trip for fire and gas alarm

Status
Not open for further replies.

bradp0024

Member
Location
Asheville, NC
I'm on an offshore oil platform where we are commissioning new temp quarters to house personnel. All feeder breakers on the platform are shunt tripped using a 24 VDC coil so everything fails open in an emergency event. For some reason the buildings were sent out with shunt trip coils in the breakers so a signal has to be sent to the breaker for it to trip. I would think that you would want to stay with a U.V. coil in this situation so if in a fire or gas event all power would be removed from the building. Also, since commissioning the buildings we've found a few of these coils bad on a few of the breakers but, you don't know this until you actually try a trip and the breaker doesn't open up. In that case a building could be powered up with a bad shunt trip coil and in an emergency the breaker wouldn't open up. Is this just engineering preference?
 