The 2020NEC says in 250.121(B) not to use the building steel as a Equipment Grounding Conductor. In NEC 800.100 it describes and shows a picture of Communication equipment being connected directly with a bonding conductor to the IBT or the Electric Grounding Conductor. The TIA Standards says in 6.3.6.1 the building steel may be used as a equipment bonding conductor subject to local codes which would include the NEC.
It would appear as if we can't use it per the NEC
What do others think?
It would appear as if we can't use it per the NEC
What do others think?