(2020) Table 310.16 is labeled "Ampacities of Insulated Conductors with Not More Than Three Current-Carrying Conductors in Raceway, Cable, orYes bundling is bundling so the same rule you mentioned would apply to using cable ties in a panel.
The bold part applies to conductors bundled within the panel.310.15(C)(1) does say "The ampacity of each conductor shall be reduced as shown in Table 310.15(C)(1) where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables not installed in raceways are installed without maintaining spacing for a continuous length longer than 600 mm (24 in.)."
Hence my question as to whether that was really the intention, or if it should read "not installed in raceways or enclosures."The bold part applies to conductors bundled within the panel.
Yes the exception applies if you meet the 10'/10% requirements.Yes but my question was about the exception. 310.15a2ex) as it applied to conductors in a panel. Not necessarily this rule
Bundled conductors require derating, the exception allows one to ignore the derating requirement when certain conditions are met.What does 310.15(A)(2) excep. have to do with bundling?
Yep, that hit me after I posted.Bundled conductors require derating, the exception allows one to ignore the derating requirement when certain conditions are met.
That is the intention as in the 2014 code the section title was changed from "More Than Three Current-Carrying Conductors in a Raceway or Cable" to "More Than Three Current-Carrying Conductors" because the section covers all locations where conductors are installed without maintaining spacing.Hence my question as to whether that was really the intention, or if it should read "not installed in raceways or enclosures."
Cheers, Wayne
IMO panels and switchboards should be exempt but they aren't. I would consider this bundling:How do you determine bundling in a panel. Heck most panels are more than 24" so are we suggesting that bundling must occur there. There is so much air inside a panel as opposed to a raceway that it seems unwise to include a panel.
Is the only time it is considered bundling in a panel is if there are tie wraps around the conductors? There is definitely space between the conductors, IMO so I don't see it applying
Was that your proposal?That is the intention as in the 2014 code the section title was changed from "More Than Three Current-Carrying Conductors in a Raceway or Cable" to "More Than Three Current-Carrying Conductors" because the section covers all locations where conductors are installed without maintaining spacing.
Now agreed.I would consider this bundling:
I don't think I have ever wire-tied wires in a panel like that.I would consider this bundling:View attachment 2559298