DUCKMAN said:iwire said:If it is a series wired circuit it makes no difference where the resister is located.
Except a short in the wiring would not be enunciated at all.
I already mentioned I was wrong, but thanks anyway.
DUCKMAN said:iwire said:If it is a series wired circuit it makes no difference where the resister is located.
Except a short in the wiring would not be enunciated at all.
LarryFine said:Then someone wired them wrong, and they cannot function as line-supervision devices. The resistors provide neither an open circuit nor a closed circuit, but a known impedance, so either a line break or short can be detected.
With them wired across the last device in the paralleled two-conductor sensor circuit, a damaged-open wire will cause a trouble signal, while a tripped sensor, which closes the circuit, will signal an alarm condition.
Hope you are not using 10% resistors ?gar said:080411-2043 EST USA
I can build a normally closed dircuit with a termination resistor at the far end of the loop. Any deviation from the expected line resistance, defined by that resistor, can then cause an alarm or trouble signal. One could use +/- 5% for a trouble signal and anything greater than +/- 10% could be an alarm. How effective such a system is to prevent a knowledgeable intruder will depend upon time constants and their knowledge.
However, it can be very useful in detecting bad wiring, including shorts or opens, or high contact resistance.
.