Jrz
New User
- California
- Electrician
Would a 2 inch concrete cover on a PVC conduit allow to reduce the burial depth from 18” to 12” or would it still be 18”?
Column 3
Nonmetallic Raceways Listed for Direct Burial Without Concrete Encasement or Other Approved Raceways
Line 2
In trench below 50 mm (2 in.) thick concrete or equivalent: 12"
Does Line 2 state that the 2" of concrete or equivalent has to be above the trench, or could you pour 2" of concrete over the pipe then backfill the rest with dirt? Line 4 uses the verbiage exterior slab which means to me that the concrete is above the trench. Nothing like that is stated in Line 2.Yes. Look at T300.5. Column 3 is for PVC. Without the concrete it's 18". Line 2 is for concrete above the trench.