E e518 New member Feb 24, 2006 #1 i have an issue,i say 120 volt gfci protected pool light,in 1" pvc conduit,need only be 12" deep as shown in table 300-5 ?
i have an issue,i say 120 volt gfci protected pool light,in 1" pvc conduit,need only be 12" deep as shown in table 300-5 ?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Feb 24, 2006 #2 Re: burial depth pool light 120 volt gfci protected Is this an article 680 application? If so 680 modifies the rules in Chapters 1-4. See 90.3 and then go to 680 for your answer.
Re: burial depth pool light 120 volt gfci protected Is this an article 680 application? If so 680 modifies the rules in Chapters 1-4. See 90.3 and then go to 680 for your answer.
jwelectric Senior Member Location North Carolina Feb 25, 2006 #3 Re: burial depth pool light 120 volt gfci protected Would that be 18 inches from the top of the pipe to the top of the dirt or would that be 18 inches from the top of the pipe to the top of any poured concrete or pavers that might be installed? [ February 25, 2006, 08:20 AM: Message edited by: jwelectric ]
Re: burial depth pool light 120 volt gfci protected Would that be 18 inches from the top of the pipe to the top of the dirt or would that be 18 inches from the top of the pipe to the top of any poured concrete or pavers that might be installed? [ February 25, 2006, 08:20 AM: Message edited by: jwelectric ]