when installing pvc under a slab inside a building what is the correct cover requirement?
roger said:Zero, see 300.5.
Roger
roger said:Zero, see 300.5.
Roger
jwelectric said:In defense of Roger just laying it on the ground would not be 0? of burial.
Notes:
1. Cover is defined as the shortest distance in millimeters (inches) measured between a point on the top surface of any direct-buried conductor, cable, conduit, or other raceway and the top surface of finished grade, concrete, or similar cover.
To just lay it on top of the ground would be an above ground installation.
Dennis Alwon said:I was saying that zero inches deep means the top of it is flush with the slab. So you think zero inches is correct?
to be "under a slab" would mean that the PVC would be under the "slab on grade" it could be touching the bottom of the concrete and would not need any coverage of earth, stone, or what have you, in otherwords, zero coverage per 300.5when installing pvc under a slab inside a building what is the correct cover requirement?
John Valdes said:I always attach the conduits to the rebar or wire mesh with tie wire. Holds it in place and insures conduit is encased in concrete.
roger said:Dennis, the question was, to be "under a slab" would mean that the PVC would be under the "slab on grade" it could be touching the bottom of the concrete and would not need any coverage of earth, stone, or what have you, in otherwords, zero coverage per 300.5
Roger