Look at 300.6(A) and 300.6(A)(3).
Look at 300.6(A) and 300.6(A)(3).
Yet Article 348 says FMC shall not be used underground or embedded in concrete.
According to the web link it is #6 or #8. See it a lot on older services. You would use an ac connector in the panel and a ground clamp for the rod or water that also has the strap for the armor.:lol:
I am curious to about this armored ground wire... Would the armor jacket have to be terminated in an AC connector? it seems to me this would be pretty difficult outside of a panel... Also I thought that#4 did not require physical protection.. perhaps I am confusing my codes. What installations would require an armored ground wire?
It’s not FMC, it is a cable assembly like AC or MC.
It’s not FMC, it is a cable assembly like AC or MC.
Holding the BAG!Where is 'like AC or MC' in the code book?
Look at 320.2 and 330.2
Both AC and MC are to be fabricated with insulated conductors. So BAG can't be either one of those. What's that leave?
Where is 'like AC or MC' in the code book?
Look at 320.2 and 330.2
Both AC and MC are to be fabricated with insulated conductors. So BAG can't be either one of those. What's that leave?
Thinking the same thing.
Back in probably the 40's they did use a version of that with an insulated conductor (RW or RHW?) that you still run into every once and a while. Used to see that buried out to a ground rod.