This LB is for service conductors after a meter base and it then enters the structure and terminates just inside the basement wall. It is going to be buried either by dirt or gravel. Is the LB allowed to be buried where the top is approximately 12 inches below grade and the bottom is approximately 18 inches below grade ? We have several different opinions. This is installed according to the 2008 NEC. 314.29 and states "Boxes, conduit bodies shall be installed so that the wiring contained in them can be rendered accessible without excavating sidewalks, paving, earth or other substances used to establish finish grade. Exception Listed boxes shall be permitted where covered by gravel, light aggregate or soil if their location is effectively identified and accessible for excavations."
Some of us believe that this LB cannot be buried and others believe they can be buried with no concern for depth and still others believe they can be buried just under the finish grade a few inches. If the code states "LISTED" in the exception, does this allow the LB to be buried?
Any guidance is appreciated so it can either be buried or installation done differently.