oldsparky52
Senior Member
- Location
- Wilmington, NC USA
I understand not wanting to fight the battle, but I think the inspector does owe you a code reference or local amendment reference to back up that position.No, but I spoke with the electrical inspector and he (rightly or wrongly) said a disconnect is required for the above situation. I think he is wrong, but I'm not fighting this battle.
230.70 requires a service disconnect to disconnect all conductors in a building from the service-entrance conductors.
230.70 (A)(1) allows for the service disconnect to be located inside the building nearest the point of entrance of the service conductors.
I might not fight this, but I sure would discuss it with the AHJ to get "clarification" on how they came to this position