Hello all,
Just want to confirm I did right with this repair (with the exception of installing an arc fault interrupt ??)
Gentleman called about exterior gfi recpt with "scorch" marks.
I went, yes there where scorch marks on building (couple inches).
Vertical GFI fs box cvr. Flush mounted. Plastic old work box.
Cover was alittle scorched, opened cover receptacle face was Burnt.
Removed cover and receptacle.
As I had the receptacle in my hand and was pulling it out of the box, there was sparking and flames running around across the bottom of the receptacle (line connection side, no load wires, hot was detached and floating, and arcing also across the receptacle plastic) and the internal area of the box.
I'm not sure if it was a loose connection that did this. I can't tell because of the melt down but the screw on the receptacle still seemed tight. The hot was off. Could it have broke off from maybe a poor strip and knick in the wire? The back of the receptacle has had a great deal of melt down at the bottom where the line connections were made, but the face of the receptacle seems that the fire burnt up and the down part was un effected.
Any possibility that the internal electronics burnt and it wasn't a loose connection or poor termination (any known issues or recalls?)? The owner said the receptacle and addition went on in the 90's.
The breaker. It did not trip as I'm speculating there was no ground fault and the sparking and flames where "just" a load on the circuit but no "overcurrent".
Is carbon that combustable that fire was just running around the box as it did (wish I had a picture of that).
I'm also speculating that an arc fault device would have picked this up and de-energized the circuit??
I stripped back the wiring to non damaged nm. Replaced the plastic box. Installed new gfci receptacle.
Should I feel good with this repair? Should I install an arc fault, or is it just another 15 amp non arc fault protected circuit like in the rest of the house and world?
Thank you
Thank you