Re: Bury depth for feeder cable
Hi,
I just put in underground here in So. Cal.
The Edison requirement was this:
3 inch dia conduit buried so that the top of the conduit was at least 30 inches below grade. Any other conduit buried in the same trench
( phone, cable etc. ) had to be at least 12 inches above the 3 inch service conduit.
Hope this helps